Author Topic: Compressor Short Cycles - Maytag MSF25D2EAW00  (Read 137 times)

Offline Blaiser

  • Technician
  • Member Since: Jun 2011
  • Posts: 790
  • Country: us
    • Buy me a beer through paypal
Compressor Short Cycles - Maytag MSF25D2EAW00
« on: September 24, 2020, 07:31:49 AM »

Need a little help here with this Side by Side Maytag Refrigerator #MSF25D2EAW00 just replaced the Compressor with a New one - Replaced the Drier filter. Blew through the Filter with Nitrogen on the Filter High Side and Opened up the Service Valve to see if Nitrogen was flowing through - then repeated the process from the Service Valve and opened up the High Side Valve from the Drier Side - everything blew through nicely. Pressurized the system with 250lbs. of Nitrogen and it stayed there for at least an hour - no leak. Pulled a Vacuum for 1/2 hour then Weighed in 5 oz. of R134A. Now the compressor is short cycling only running for about 1 minute then shutting down. Put an amp meter on it and it's pulling 5.6 - 5.8 amps??? Any thoughts? Compressor will try to kick back on but only run for 1 minute?? Thermostat up all the way??
« Last Edit: September 24, 2020, 07:33:15 AM by Blaiser »

Offline Repairs.pridehvac

  • VIP Member
  • Member Since: Jul 2019
  • Posts: 15
  • Country: 00
Re: Compressor Short Cycles - Maytag MSF25D2EAW00
« Reply #1 on: September 24, 2020, 01:37:01 PM »
Did you install a new start device?

Offline Repairs.pridehvac

  • VIP Member
  • Member Since: Jul 2019
  • Posts: 15
  • Country: 00
Re: Compressor Short Cycles - Maytag MSF25D2EAW00
« Reply #2 on: September 24, 2020, 01:40:35 PM »
250psi of nitrogen is a lot. Whirlpool actually doesn't recommended using nitrogen for any sealed system repair or test. The most I would do would be 120 psi. You may have a failed compressor.

Offline Dash

  • Technician
  • Member Since: Sep 2015
  • Posts: 79
Re: Compressor Short Cycles - Maytag MSF25D2EAW00
« Reply #3 on: September 24, 2020, 10:30:36 PM »
That's a lot of current, as if start winding isn't dropping out.  What's the low side static pressure?

Offline Blaiser

  • Technician
  • Member Since: Jun 2011
  • Posts: 790
  • Country: us
    • Buy me a beer through paypal
Re: Compressor Short Cycles - Maytag MSF25D2EAW00
« Reply #4 on: September 25, 2020, 08:07:18 AM »
2-4 psi. on low side - New Compressor states 2.2 amp on sticker tag running amps??