Author Topic: Tempstar heat pump all running no cool air  (Read 1730 times)

Offline lgmccoy1

  • VIP Member
  • Member Since: Feb 2008
  • Posts: 13
Tempstar heat pump all running no cool air
« on: June 28, 2015, 11:22:09 AM »

I have a 3.5 ton Tempstar split heat pump.  Thermostat is set to cooling.  Both air handler and condenser fans are running. No cool air is coming from vents.  My copper refrigerant lines are just air temperature.  I know the large line should be cold and small copper line warm.  Both are neither.  No warm air is coming from condensor fan either.  Have did ohm check on compressor windings.  Have continuity on all terminals.  C to R is 2.0-2.5 ohms, C to S is 2.0-2.5 ohms, R to S is 3.5-4.0 ohms.  Compressor gets very hot to touch after running for a few minutes (not sure if this is normal).  Have checked start capacitor with ohm meter and all terminals are open.  I am a basic troubleshooter and have limited knowledge on HVAC.  I thought it might be low refrigerant but I thought low pressure cut off would prevent condensor unit from coming on if this was the case?  Thanks in advance.

Offline rabjr01

  • Technician
  • Member Since: Nov 2014
  • Posts: 16
  • Country: us
Re: Tempstar heat pump all running no cool air
« Reply #1 on: June 30, 2015, 03:02:28 PM »
yes it sounds like low charge the LPS is meant to prevent the compressor from running in a vacuum. it may also be a bad capacitor testing one is easy with a analog meter or one that will check continuity with a beep. switching the test leads back and forth on the c and herm terminals will cause a short beep or a sweep of the needle with it falling to open with an analog meter

Offline lgmccoy1

  • VIP Member
  • Member Since: Feb 2008
  • Posts: 13
Re: Tempstar heat pump all running no cool air
« Reply #2 on: June 30, 2015, 03:17:24 PM »
Found the problem.  Ended up being a leak in two tiny copper lines inside the air handler where the return is located.  These two lines were touching and over time vibration caused them to rub and create a tiny pinhole in each.

Offline rabjr01

  • Technician
  • Member Since: Nov 2014
  • Posts: 16
  • Country: us
Re: Tempstar heat pump all running no cool air
« Reply #3 on: July 01, 2015, 10:26:43 PM »
Glad to hear it line rubs are common

 

Tempstar Heat Pump not running but Air handler is

Started by lgmccoy1

Replies: 4
Views: 9886
Last post November 19, 2010, 06:16:05 AM
by jumptrout51
Tempstar heat pump won't initiate defrost cycle

Started by lgmccoy1

Replies: 13
Views: 18155
Last post December 24, 2010, 12:53:31 PM
by jumptrout51
Heat Pump Defrosting

Started by Icehouse

Replies: 3
Views: 8124
Last post December 27, 2008, 03:57:05 AM
by Icehouse
Heat Pump Electrical Componet Check

Started by Icehouse

Replies: 1
Views: 10044
Last post February 25, 2009, 08:00:45 AM
by thermodix
Goodman Company Reannounces Recall of Air Conditioner/Heat Pump Units

Started by AJ

Replies: 0
Views: 7420
Last post December 08, 2009, 03:52:04 PM
by AJ
Carrier Heat pump OAT 25HPA

Started by chrissymustang

Replies: 4
Views: 8805
Last post February 02, 2011, 05:21:06 PM
by chrissymustang